Hi there,
Save hours of searching online or wasting money on unnecessary repairs by talking to a 6YA Expert who can help you resolve this issue over the phone in a minute or two.

Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.

Here's a link to this great service

Good luck!

Posted on Jan 02, 2017

Ad

Fahr Quad

  • 736 Answers

SOURCE: Ground Fault circuit Breaker trips each time a load is applied

The most likely causes in their order of probability are: 1) water somewhere in the circuit causing the hot wire to ground; 2) a legitimate trip caused by a defect in a device plugged into the circuit; and 3) a defective GFCI breaker. In the first case, wait until it has been dry for about a week and see if it trips. In the second case, make sure there is nothing plugged into the circuit and try resetting. In the third case go ahead and put the regular breaker in, then put a GFCI outlet into the first box downstream from the breaker. If installed according to the directions, that outlet should protect all of the outlets downstream.

Posted on Feb 27, 2009

Ad
co7196

Ned C Cook

  • 3433 Answers

SOURCE: GFI on cord trips out.

Probable cause is a single pole gfi opposed to a double pole gfi.
* Do not use a single pole GFCI ON A MULTI WIRE CIRCUIT, IT WILL NUISANCE TRIP IMMEDIATELY
Use a two pole GFCI circuit breaker on such circuits.

Posted on May 20, 2009

protek480

Craig Butler

  • 1730 Answers

SOURCE: swimming pool light on a gfi breaker

It won't take much to trip the GFI. Have you tried to dry the fixture out completely? Use a blow dryer and remove any moisture. Also, remove the light and cap the wires and try it if you can, it might be the wire.

If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c

Posted on Jul 23, 2009

logcabinsam

  • 7 Answers

SOURCE: ground fault interrupt (GFI)

I have a Whirlpool Model AD$)DSR1 Dehumidifier, with similar issues. When plugged in where it was operating for three years with no problems, it would trip the gfci within 10 minutes. I have it out in the garage right now with all the covers off, and I've had it running on a heavy duty outlet for about a half hour now. The compressor is too hot to touch (ouch!), and the condenser coils are only cool, when they should be quite cold. I am ready to judge that one of two things has happened: Either the compressor is bad, or the refrigerant has leaked out of the system.

Posted on Aug 27, 2009

Anonymous

  • 2 Answers

SOURCE: trips ground fault on plugging into receptacle

I just opened one of the machines with this issue and found that the heating element is entirely ripped open (over the length of the coiled heating element) and the water contaminated with brownish stuff from within the element.
Was wondering if that part can be replaced.

Posted on Nov 30, 2009

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

LG Refrigerator LSC27931ST trips GFI. Unplugged a plug with Black, Brown , Blue and purple wires feeding the water solenoids and defrost heater. Power stayed on. Help


If power is still staying on how can it be tripping the GFI? Dead short somewhere and no power should be coming into the unit since the GFI is the house source.

May 08, 2017 | Cars & Trucks

1 Answer

Sta-rite heater is about a year old. It worked well up until a week ago. It now trips the gfi breaker. I swapped out the breaker and it trips that too. If I disconnect the exhaust fan, the heater powe


Something in the electrical system supplied by the GFI breaker has a ground fault. The current to ground required to trip a GFI is very little such that dampness on any electrical connection can trip it. This is especially true with motors that have a lot of fine wires in the windings and are open to allow cooling.
Hard water and pool chemicals all are worse than condensation from the air because of their ionic nature.
If the same GFI powers the pump it is what I would suspect first. Your question got cut off before the result of the fan disconnect which if disconnected didn't trip the GFI, is probably the problem. But you should open whatever you can access containing electrical components and make sure everything is dry

Feb 07, 2015 | Sta Rite Pool & Spa

1 Answer

What would cause intermitant pop of ground fault. only thing on the line. ground fault has been replaced


Refrigerators are not recommended to be plugged into a GFI outlet. Depending on the age of the fridge there will be spikes in the current the fridge uses at certain times causing the GFI to trip. A GFI outlet is much more sensitive to current than a non GFI outlet that is tied back to the the regular breaker in the electrical panel. Pleazer Appliance...

May 06, 2014 | Whirlpool Refrigerators

1 Answer

Our 7788F keeps going into a ground fault condition. Need help troubleshooting. John


Ground Fault ???
Troubleshooting Ground Fault

Troubleshooting a ground fault circuit interrupt, or GFI, breaker is pretty straightforward. Troubleshooting the circuit itself can be quite time-consuming.
The GFI breaker is designed with a test button incorporated into the breaker itself.
Pushing the test button should trip the breaker.
On GFI-style breakers the neutral wire going into the house's outlets is connected to the breaker's neutral connector, the white neutral that comes out of the breaker is connected to the neutral bus in the panel, isolating the neutral bus from the neutral wire going into the house.
The test button actually shorts the neutral wire feeding the circuit to the neutral bus in the electrical panel creating a ground fault that should trip the breaker.
It is considered a ground fault because the neutral bus in the main electrical panel is actually connected to the ground bus through the panel's metal casing. What to do if the test button isn't tripping the breaker
1
Push the test button on the GFI breaker.
The breaker should trip.
If the breaker does not trip, then it may be that the breaker has already tripped and just looks like it's on.
The position of the switch may only move slightly from the on position towards the off position when tripped.

2
Push the switch on the GFI breaker all of the way toward the off position.
It may take some force to get the breaker to reset.
Turn the breaker back to the on position.
When the breaker has been reset properly you should feel some resistance when pushing the switch back on.



3 Push the test button again and the breaker should trip.
If the breaker still doesn't trip then you should test for power at the screw connections inside of the electrical panel.
Remove the screw that holds the dead front covering the breaker's connections.
Remove the dead front cover.

4
Test for power with your voltmeter set on AC volts on the highest scale.
For a single pole GFI breaker, touch the black lead from the tester to the silver screw on the GFI breaker and touch the red lead from the tester to the brass screw on the GFI breaker.
You should see 110 volts on the tester. If voltage is seen but the test button won't trip the breaker, then the breaker is bad and should be replaced.

5
Test for power on a two pole breaker by touching the red voltmeter lead to one of screws with a black or red wire connected to it.
Touch the black lead to the other screw with a black or red wire connected to it.
You should read 220 volts or close to it on your voltmeter.
If you read voltage and the test button won't trip, the breaker is bad and needs to be replaced.

What to do if the breaker won't reset and keeps tripping when turned on
6
Unplug everything that is plugged into any of the outlets on the circuit in question.
Try resetting the breaker again by pushing the switch all the way to the off position and then turning it back to the on position.
If it won't reset and trips when the breaker's switch hits the on position, it could be a bad breaker or a problem in the circuit itself.
7
Use your straight-tipped screwdriver to loosen the brass connection screw or screws on the GFI breaker.
Pull the black hot wire, or wires, out of the breaker's connectors.
Loosen the silver screw the white wire is connected to and remove it from the GFI breaker.

8
Push the switch all the way to the off position.
Turn the switch back to the on position.
If the breaker still won't reset, then the problem is the breaker itself and it should be replaced with a new one of the same size, brand and model.
If the breaker resets normally and the test button trips the breaker when pushed, the problem is in the circuit itself and an electrician should be called to find your ground fault.

9
Reconnect the black wire, or wires, to the brass screws on the GFI breaker.
Reconnect the white wire to the silver screw on the GFI breaker.

10
Replace the dead front cover into the breaker panel.
Install the screw or screws that hold the dead front in place.



http://www.hilo-electric.com/blank?pageid=63

Aug 14, 2013 | Computers & Internet

1 Answer

Is a house plug with a cfic braker light suppose to be red or green


Most are green when functioning properly. Many have no lights at all. Try depressing the reset and see if the outlet works again. If not there are other things to look for. Often times one GFI outlet feeds multiple more outlets from the "load" connection on the back side of the GFI. If there is something wet, overloading the rating, or something with a fault in any of the outlets multipled off the single GFI it will trip. Disconnect all devices then attempt to reset. If that doesn't work and you possess some electrical skills pull the GFI outlet and disconnect the wires going to the "load" connection (While power is off) Re-energize and attempt to reset the GFI Outlet. If it resets your problem is beyond that outlet in the circuit of what you disconnect. You may not have found all the affected outlets. FYI if you have a 15amp GFI the rule of thumb is you can put more devices on outlets working off or through the GFI that add up to more than 1500 watts. If it is a 20amp GFI a quick rule of thumb is no load over 2000 watts. Space heaters, blow dryers, and hair curlers are often 1800 watts each. One alone and can trip a 15 amp GFI.

Dec 28, 2012 | Zyxel PLA-401 v3 - Bridge - Ethernet, Fast...

1 Answer

What's youI just wired in my J-300 Jacuzzi hot tub. The GFI trips every time I reset it. I took the GFI out of the equation and the tub runs fine, does not trip the breaker at the main breaker box


#1. DO NOT GET INTO TUB FULL OF WATER WITH A GROUND FAULT.
2. There is a short. You need to get multimeter and start checking each part for current running to ground wire.
3) Power is ON. Connect power without GFCI.
4) Tape tester leads to wood sticks to keep hands away from power.
5) Do not touch anything directly or you will become the ground rod.
6) Ground wire must be present, and bonded back to main panel box.
7) Do not sit or touch directly on cement or bare ground. Do not touch or lean into anything made of metal.
8) Body and parts must be on sheet of plywood, or similar non-conductive dry surface.
9) Test each part with spa, but also test electric line coming from main box.
10) GFCI will also trip with any fault detected on line. So the wire coming to spa may have the fault.
11) Add a new dedicated line from main box to spa.

http://waterheatertimer.org/How-to-wire-GFCI.html
http://waterheatertimer.org/See-inside-main-breaker-box.html

If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7

Oct 02, 2012 | Electrical Supplies

1 Answer

Why does he GE profile top load washer trip my GFI circut half way thru it's scan cycle


Earth leak either due to water in something or a ground fault in the motor is my guess. It may even be a motor windings fault that is building up resistance as it warms up. You need a service engineer with a good test meter,

Nov 18, 2017 | General Electric Profile WPGT9150 Washer

2 Answers

My Sylvania - ground fault 15 amp breaker (32740) is tripping with minutes of reseting. It is for 3 washrooms & hallway & is 30 years old .....does or can it loose its life span? What is the cost...


A circuit breaker can go bad, but usually not in the way that you describe. That's not to say that it can't happen, but just not typical. GTE Sylvania breakers were once popular - I installed quite a few GTE / Sylvania electrical panels in homes in the late 80's. You may have trouble finding replacements; do not put an breaker that "fits" into the panel, unless the breaker is designed for use in the panel you have.

The first thing to do is determine the source of the problem. The breaker will trip, but not indicate if it was the result of a heavy electrical load or a ground fault condition. A 15 amp circuit breaker is designed to carry up to 12 amps continuously. The greater the load, the more quickly it will trip. it may carry a 14.5 amp load for several minutes to an hour before tripping, and a 20 amp load may be carried a second or two. GFI breakers are designed to carry 5 thousandths (.005) of an amp (or 5 milliamps) to ground, or the 12+ amps to neutral before they trip.

The way I would attack the problem is to install a new GFI outlet in front of the old wiring, by "inserting it" between the panel and the other plugs and lights, switches, etc on that circuit. The GFI outlet will provide the same GFI protection that the circuit breaker provided at a fraction of the cost.

Turn off the old GFI breaker, and remove it completely. Install a new, standard (non-GFI) single pole 15 amp circuit breaker in its place. Completely remove from the panel the cable that the old GFI breaker fed. Buy a new electrical outlet box (surface or flush mount as desired) that is large enough and deep enough for a GFI plug and 2 cables (if surface mount, use a 4" square deep box and appropriate cover - or if flush mounting use a deep plastic / fiber single gang box). It will be installed in a place close to the panel, but where the old cable will be able to reach inside. Bring the old cable removed from the panel into the new box. Run a new cable that has the same number and size wires from the panel into the new box, too. Connect the circuit neutral and circuit ground to the neutral and ground bars in the panel (they are probably the same bar) and the hot wire to the circuit breaker. make sure that the circuit breaker is OFF. Twist the two ground wires together and combine an 8 inch length of bare or green insulated wire with them in a wirenut.

Next, wire a new GFI plug in the new box. Connect the green wire from the wirenut to the green terminal of the GFI outlet.

Connect the plug's LINE terminals to the neutral and hot wires in the cable that you ran from the panel to the outlet box.

Now, connect the GFI plug's LOAD terminals to the neutral and hot wires in the cable that you removed from the panel and reinstalled into the new outlet box.

Secure the GFI outlet into the box and install the cover. Cover the electrical panel.

Power up and test. if the GFI trips, there's a ground fault in the circuit. If the circuit breaker trips, the circuit is overloaded.

Jun 13, 2011 | Your One Source Qo Single Pole Ground...

2 Answers

Purchase new 32'' tv 2-day ago, will not work in a GFI plug outlet trips GFI each time you reset, is there something wrong with unit? works fine in a non GFI outlet


Good News!!! GFI outlets are made to trip when a large amount of power is pulled through them. A GFI is basically a small circuit breaker.Your television set is probably just pulling more amperage than the GFI is rated to handle. That means the GFI is working properly And so is the TV!

May 05, 2011 | Televison & Video

1 Answer

Hi, I have a Kenmore top freezer refrigerator model number 363.79567990. The freezer stopped working and I found out that I had to press the "Reset" button on the outlet while it was unplugged...


It sounds like you've plugged your fridge into a GFI (ground fault interrupter) outlet.

The National Electrical Code (NEC) article 210.8 A (6) says in dwelling units, only those outlets in a kitchen (I'm assuming your fridge is in the kitchen - right?) "where the receptacles are installed to serve the countertop surfaces" must be provide ground fault protection aka "GFI outlet". Unless your town, city, county or state has laws that supersede the NEC, you should have the outlet changed to a standard, grounded outlet to prevent the nuisance tripping you are experiencing when the cooling compressor is trying to start. A refrigerator is not a counter surface appliance, and therefore does not require GFI protection.

The other outlets are fed from this outlet, so when you connect the fridge to another outlet on the circuit, the same GFI plug trips again. When you replace the GFI plug with a "regular one, the GFI plug should be installed in another outlet to provide the GFI protection needed in the kitchen - as described in the NEC above. If you are not familiar with how to do this, please, call a licensed electrician to do this very important job for you. Be safe & be smart.

I hope this helps!

Nov 01, 2010 | Kenmore 55612 / 55614 / 5561 / 655619 Side...

Not finding what you are looking for?
Refrigerators Logo

Related Topics:

47 people viewed this question

Ask a Question

Usually answered in minutes!

Top Refrigerators Experts

John Tripp
John Tripp

Level 3 Expert

4656 Answers

Marvin
Marvin

Level 3 Expert

85206 Answers

Brad Brown

Level 3 Expert

18108 Answers

Are you a Refrigerator Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...