Condenser fan shuts off after 15 second all the coil gets hot compressor continues to run vrv3 daikin

Posted by on

Ad

6 Suggested Answers

6ya6ya
  • 2 Answers

SOURCE:

Hi there,
Save hours of searching online or wasting money on unnecessary repairs by talking to a 6YA Expert who can help you resolve this issue over the phone in a minute or two.

Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.

Here's a link to this great service

Good luck!

Posted on Jan 02, 2017

Ad
  • 56 Answers

SOURCE: Food and water freezes but ice cream is soft

Check the door gasket seal.
Open the door for a few seconds and then close.
Immediately open the door again, and, if sealing properly, it should take more pulling force to open the door.

Posted on Mar 30, 2009

Ad
  • 534 Answers

SOURCE: Amana Cooling Condensing Unit fan won't kick on

be aware that not repairing this asap that you are causing yourself more problems First I would change out the fan capacitor and see if this could be the problem. Secondly if the capacitor isn,t the problem change out the motor . By continuing to allow the system to cycle like this the compressor will take a dive on you costing more . Good Luck

Dave

Posted on Aug 04, 2009

Testimonial: "Yes, it's dual run capacitor problem. I used a stick to spin the fan blades and it starts to slowly spin and up to normal speed, so motor is good."

  • 674 Answers

SOURCE: fan wont kick on

If you are talking about the condenser fan not running, that would cause the unit to shut down on high discharge pressure. Is the indoor fan running? Check the capacitor for the outdoor fan. Also make sure the outdoor fan has power to it. If it has power and the capacitor is good then the fan motor may be bad. If the nc in your name stands for NC then it is possible I could take a look at it as I am in NC. Let me know what you find.

Posted on Jul 03, 2010

  • 351 Answers

SOURCE: I have a Kenmore Coldspot Model 106. Here's the

hi yes you are right replace it jim

Posted on Oct 11, 2010

Macmarkus
  • 2605 Answers

SOURCE: GE Profile fridge: freezer is

Hello, welcome to FixYa.

I understand based on your post you have a GE profile PFS22MIS fridge not cooling in the fridge (upper cabinet) section, correct ?.


It is possible the problem is related to the condensor fan, but not likely. The difference with these fridges and many others (especially the older fridges) is the condensor fan does not run all the time. Instead the control board at the back (pcb) tells it when to run and at what rpm to run as well, it is a variable speed fan motor...and may in fact not run at all at periods.


The one thing I'd suggest you inspect is the back wall of the freezer. You mentioned the evaporator fan motor is operating, correct ? Is there any frost build up on the back wall of the freezer section, or if not visible have you removed the back wall of the freezer ?

I will need to watch for your reply before going forward. I hope you can appreciate there are so many variables since the fridge has many factors controlling air flow which in turn determine what the possible problem and solution will be.

Sounds to me it is a damper or blocked evaporator initially at least. Let me know what you find and we'll go from there.

Regards,

Macmarkus :)

Posted on Sep 20, 2011

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

New Hisence fridge freezer noisy and hot


for the noise check the compressor groumits

FRIDGE COILS or door walls SEEM VERY HOT:


The condenser coils do get hot. They can even be to hot to comfortably touch and this is normal.

The refrigerator should not run constantly but shut off with each defrost cycle.

Running constantly and never cycling off can indicate a cooling problem.

One thing to try is to wait till it has been running a few minutes then open the door and turn your cycling thermostat towards the off position. It should cycle off before getting to the off position on the dial.

If it does not cycle off then it's not getting cold enough to satisfy the thermostat. This is likely the reason the refrigerator runs all the time.

A thermometer in a glass of water can be used to check the temperatures in the refrigerator section.

You can check that all fans are running.

the reason the outer side of the door seal area is getting hot is the compressor is over heating, probably the condenser fan motor to your compressor is bad.
It should be a little warm but not hot. they don't use heaters anymore ( some older models still use heaters) around the doors, instead they use the condenser coils to remove condensation and moister, you might want to check your condenser coils on the bottom or back of fridge to see if they need cleaning
If the condenser coils/condenser fan are all plugged up they need cleaning and/or the condenser may fail or has failed..

The ones that use an electric heater will have an "energy saver" switch that will turn it off.: God is the reason I give you free advice so God is good!

Dec 24, 2016 | Refrigerators

1 Answer

Last week told we needed new evaporator. 2nd guy: it was not the evap replaced the tubing, had 2 ob leaks. recharged, fridge worked and then heated up again. notice door center edge is hot.


FRIDGE COILS or door walls SEEM VERY HOT:

The condenser coils do get hot. They can even be to hot to comfortably touch and this is normal.

The refrigerator should not run constantly but shut off with each defrost cycle.

Running constantly and never cycling off can indicate a cooling problem.

One thing to try is to wait till it has been running a few minutes then open the door and turn your cycling thermostat towards the off position. It should cycle off before getting to the off position on the dial.

If it does not cycle off then it's not getting cold enough to satisfy the thermostat. This is likely the reason the refrigerator runs all the time.

A thermometer in a glass of water can be used to check the temperatures in the refrigerator section.

You can check that all fans are running.

the reason the outer side of the door seal area is getting hot is the compressor is over heating, probably the condenser fan motor to your compressor is bad.
It should be a little warm but not hot. they don't use heaters anymore ( some older models still use heaters) around the doors, instead they use the condenser coils to remove condensation and moister, you might want to check your condenser coils on the bottom or back of fridge to see if they need cleaning
If the condenser coils/condenser fan are all plugged up they need cleaning and/or the condenser may fail or has failed..

The ones that use an electric heater will have an "energy saver" switch that will turn it off.: God is the reason I give you free advice so God is good!














Fridge FAN CONTINUALLY STAYS ON OR SHUTS OFF WHEN DOOR IS OPENED:

NORMALLY WHEN THIS HAPPENS U EITHER HAVE A DOOR CONTINUALLY OPEN ISSUE OR A BAD DOOR SEAL LETTING AIR IN AND CAUSING FAN TO OVERWORK ITSELF. ANOTHER CAUSE CAN BE DIRTY COILS AND CONDENSER AND LASTLY NOT TO COMMON IS A SHORT IN THE FAN SYSTEM ITSELF. A MORE PROBABLE CAUSE COULD BE BAD THERMISTORS OR EVEN COLD CONTROL THERMOSTAT ( WHEN THE THERMISTORS OR THERMOSTAT DO NOT GET/GIVE A PROPER READING, THEY CAN CAUSE THE FAN TO CONTINUE TO OPERATE AS THEY FAIL TO RECOGNIZE OR REGULATE THE PROPER TEMPERATURE.

Dec 20, 2015 | Maytag Refrigerators

1 Answer

How do i get my condenser fan to stop running. it is cooling fine but won't shut off unless i shut it off.


Are you sure its the condenser fan? The fan is attached to the compressor power and wont run unless the compressor is running. On the other hand the fans inside the cooler will run 24/7 and are designed for continuous duty. If someone has worked on the compressor wiring you may have to re establish the wiring following the wiring diagram. I have seen condenser fans wired in hot areas to run continuously to attempt to cool down a hot compressor or compensate for a worn out or damaged condenser that doesn't get rid of the heat from the system. If that is the case a new condensing unit is probably in your future. Hope this helps good luck.

Oct 09, 2014 | True GDM-47 Refrigerator Merchandiser -...

1 Answer

Condenser Fan Shuts off after 15-20min, Compressor continues to run but gets hot


Condenser fan motor or motor wiring is bad. That compressor should never run without the fan. Good luck.

Jun 14, 2014 | Beverage-Air MT27 Beverage Cooler...

1 Answer

Problems associated with copeland sroll compressors in industial ai conditioning systems


There is either a valve sticking in the compressor or the orifice tube or expansion valve is clogged. Time to drain, and flush to check the orifice or exp valve. If not those then replace the compressor,.

Mar 10, 2014 | GE E Industrial System Tfn60rcp 60a Air...

1 Answer

Rangemaster sxs cream . Why is my fridge and freezer the same temp ???? If anybody could give me an answer or solution.


Jason,
MOST refrigerators get there cold from the freezer side and circulate it via a fan that's also normally inside the freezer. There are three motors normally in a refrigeration system. The inside Evaporator fan motor that circulates air across the evaporator coil inside the box, the Condenser fan motor near the compressor that cools the freon after compression, and the compressor itself. If you open the doors (and sometimes you may have to hold in the door switches) do you hear a fan running? If not you could have a couple things going on: 1. The fan(s) has failed. 2. The freezer Evap coil may of iced over and the fan too is frozen stopped. 3. Your condensing unit:(compressor, condenser fan, condenser coils) has a problem.
It is important to know if the compressor itself is running. If there is a loose connection to the compressor via the start/over load relay (normally attaches directly onto the compressor), or if the start/over load otself is bad the compressor will not run. Best way to tell is via gauges but I doubt your frig has ports. Check to see if your compressor is really hot. Could be bad start/over load relay or bad compressor. Try unplugging your frig for say 30 min then, with your hand on top of a cool compressor, plug the frig back in and see if compressor smoothly vibrates for at least 5 min without becoming very hot or shutting off even though fan continues to run. The fact your fan is running TYPICALLY means the thermostat is calling for lower temps and the fan/compressor kick in together.



If you need further help, reach me via phone at https://www.6ya.com/expert/steve_24d988f3507f7480

Oct 11, 2013 | Refrigerators

1 Answer

My 9000 Btu Kenwood Continental Series split unit shuts down compressor after every 10-15 minuits regardles of room temp. Gas pressure is OK & I have tried replacenig cooling sensor but to no use. I am...


Sounds like the compressor may be overheating. You need to check the outdoor condenser coil it may be stopped up with dirt, in turn, overheating the compressor. The condenser coil looks like a radiator and the outdoor fan blows through it, in a sense releasing the hot air from the building. If the coil is stopped up, it can not release the heat. You can wash this coil out with a hose and sprayer. Just be careful not to get the motor wet and be sure to shut off power.

Jun 24, 2011 | Kenwood Heating & Cooling

1 Answer

I have a Kenmore Coldspot Model 106.7629461 Here's the problem: When the unit needs to run to keep the freezer/refrig cold, it does so for about 10-15 seconds. Then it shuts off for about 2-3 minutes. ...


Hi,

Many times a freezer and/or refrigeratordo not work right because of a dirty condenser coil...there are also many otherthings that can go wrong. If you are hearing a clicking or buzzing then check out thelast two tips.

If your refrigerator is running but warm, then...

Check out this tip that I wrote about that... it is a great place to starttrouble shooting your unit...and something that you can do rather then callinga repair person to do a simple thing for you...

Refrigerator Condenser Coil Cleaning Refrigerator Repair

Refrigerator Troubleshooting Refrigerator Compressor

Refrigerator Compressor Start Capacitor and Start Relay
Refrigerator or Freezer not Cooling or Getting Cold

heatman101

Oct 10, 2010 | Kenmore Refrigerators

1 Answer

A/c will not continue to cool.. Starts fine, runs fine.. but shuts down cooling ( comp shuts off but fan still runs) after anywhere from 5 min to multiple hours. No circuit breakers or fuses blow. CAN...


One amateur test is to place your hand on the compressor and see if it
is too hot to hold your hand on it. You may have a restricted condenser coil
If it is too hot then the condenser coil is restricted inside the unit
if not be sure and clean condenser coils with good coil cleaner.
You can put a fan on the compressor and see if it runs for another test to confirm it
If this was helpful please rate me.

Leo Ponder Appliance-Tyler,Texas
imufo2@sbcglobal.net

Aug 22, 2010 | Dometic Rooftop RV Air Conditioner

1 Answer

Amana Cooling Condensing Unit fan won't kick on


be aware that not repairing this asap that you are causing yourself more problems First I would change out the fan capacitor and see if this could be the problem. Secondly if the capacitor isn,t the problem change out the motor . By continuing to allow the system to cycle like this the compressor will take a dive on you costing more . Good Luck

Dave

Aug 04, 2009 | Amana PTH123B25AJ Heat Pump Air...

Not finding what you are looking for?
Refrigerators Logo

Related Topics:

35 people viewed this question

Ask a Question

Usually answered in minutes!

Top Refrigerators Experts

John Tripp
John Tripp

Level 3 Expert

4656 Answers

Marvin
Marvin

Level 3 Expert

85178 Answers

Brad Brown

Level 3 Expert

18108 Answers

Are you a Refrigerator Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...