Question about Mitsubishi Mr. Slim MXZ30TN Air Conditioner

2 Answers

MSZGE12NA, OUTSIDE UNIT LED BLINKS SIX TIMES , INSIDE UNIT BLINKS CONTINUOUSLY. OUTSIDE UNIT WILL NOT RUN, INSIDE UNIT DOES. NO HEAT, COOL. CONTROL WIRE BARE "DRAIN" LINE CARRIES A LOAD THAT ARCED AGAINST OUTSIDE CABINET. THIS WIRE IS NOT ATTACHED AT EITHER END YET IS UNDER A LOAD. WHY IS A MYSTERY.

Posted by on

Ad

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Mitsubishi Master
  • 2,410 Answers

Sounds as if the insulation has melted and two bare wires are touching .

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

Posted on Dec 28, 2017

Ad

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Loyalty:

    Visited the website for 30 consecutive days.

  • Master
  • 572 Answers

Those blink is a code and you can look at the unit wiring diagram section and it would tell you what those code mean

Posted on Dec 27, 2017

Ad

5 Suggested Answers

6ya6ya

6ya staff

  • 2 Answers

SOURCE:

Hi there,
Save hours of searching online or wasting money on unnecessary repairs by talking to a 6YA Expert who can help you resolve this issue over the phone in a minute or two.

Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.

Here's a link to this great service

Good luck!

Posted on Jan 02, 2017

Therinnaiguy

Chandler Ede

  • 1420 Answers

SOURCE: no cooling after power out, indicator lights pattern not in manual

The Mitsubishi units have to be reset by turning off the indoor units by switching the remote or thermostat to off. Then turn off the breaker to the outside unit(s). After 30 seconds,turn on the breaker and then you can turn on the remote for cool. If no lights come on on the inside units, most likely you have blown a fuse soldered on the main PC board. At this point, call your technician. A goos tech will be able to wire in an in-line fuse holder so if it should happen again, you can easily replace the fuse. If you do see a light or two come on at the indoor unit but the outdoor unit does not start after 3 or 4 minutes, sounds like you will need to call a technician. Most likely you have a blown fuse on the main PC board of the outside unit. It is not an easy one to replace. Good Luck!

Posted on Sep 04, 2007

Anonymous

  • 11 Answers

SOURCE: split system outside unit won't come on for cooling, only heating

Check your filters, dog hair and lack of maintenance will definitely burden the cooling mode of the Mr Slim units.

Posted on Aug 24, 2009

matyt94

  • 81 Answers

SOURCE: inside unit turns on, outside doesn't

Could be a wiring problem or a lack of refrigerant. All you can do is professionally have the unit checked and serviced.
Hope this helps I take the time to answer your question so please rate me

Posted on Jun 28, 2010

mrbenz7

  • 12 Answers

SOURCE: outside unit do not run.Red light blink 6

That is a trouble code signalling that your unit needs service. It is time to call a professional for help!

Posted on Jul 21, 2010

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR


14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
continuously - • Indoor PCB
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
tection 4 times occurance
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
tion 4 times occurance
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• IPM (Power transistor)
• Compressor

Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.

Oct 13, 2017 | Panasonic Heating & Cooling

1 Answer

CHH012CD-13B


This type of unit does not drain into the outside unit. It drains into a nearby interior drain, or just to the outside near Inside unit. If the unit is cooling properly, you're ok.

Jul 01, 2014 | ComfortStar CHH012CD-13B Wall Mounted Mini...

1 Answer

No heat but fan keeps running


If the air conditioner compressor runs all the time the main control board might be defective. The main control board provides the voltage to the fan motor and compressor. These boards are often misdiagnosed. Check all other components to be certain this is the cause of the problem.

Nov 25, 2013 | LG LAN186HV / LAU186HV 18,000 BTU 15 SEER...

1 Answer

I have a Rheem Heat Pump unit. This winter, the outside unit fan at times trips off, but the inside unit keeps running continuously. I woke up one morning & it was 62 in the house. The inside unit ran...


Dear Friend!

Due to very low ambient temp, the fan will not run. Once the pressure build up, it's automatically run for some time and again cut off. But if you keep Heat mode and still tem not raised in your room means the reversable valve not working and hence the compressor and out side fan also will not work. Keep "Heat" mode and temp setting +29 to get better heat. Hope is it helpful?

Dec 10, 2010 | Heating & Cooling

1 Answer

Rheem heat pump,have to keep pushing red reset button for fan


Either the fan motor is going out OR the compressor may need a boost of power from a quick start.

When the compressor gets old, sometimes it requires a little extra power to get it going.

Your unit should be under work warranty if they installed it.

Jan 06, 2010 | Heating & Cooling

1 Answer

I just installed a ductless mini split 12000. when I put power to it the outside unit compresser runs no fan the led read out just blinks very fast the remote does't do any thing


One thing you need to check is Polarity. the 2 wires red and white, need to be on the same terminals inside as they do outside. this is very important.

Oct 28, 2009 | LG LS-L1210HL 12000 BTU Heat and Cool Mini...

1 Answer

I have a 1995 Sear garage door opener that stopped working


The trolley (the part that moves back and forth and is connected to your door) of your opener is most likely jammed against the bolt just in front of the motor unit. You can remove the bolt or loosen the chain until your unit will run. Once the door is closed find the 'up limit' on the side of the motor unit and turn it about 3 turns in the opposite direction of the arrow printed on the cover. Now replace the bolt or tighten the chain. Whichever you first did.

May 28, 2009 | Sears Craftsman LiftMaster Chamberlain...

1 Answer

AIR CONDITIONER LG S18AN


The operating LED will be blinking 5 times, means that there is a
comunication error (serial comunication) between the outdoor and the indoor unit.

Dec 28, 2008 | LG LS-K1830CL Cool Mini Split Air...

1 Answer

KELVINATOR KSR20C


One might think so, YES! look on one of the door panels that you can remove! Thank-you-very-much!

Aug 02, 2008 | GE Zoneline AZ38H12DAD Split System Air...

2 Answers

Lg ductless no ac


I may not be of much help but I may be able to guide you into some diagnosos. If there is a communication problem between the inside and outside unit, both on the inside and outside units a colored LED will bling 5 times then pause for 3 seconds. The 33 and 44 codes are confusing to me because I have never seen this. Try resetting the outside unit with no call for heat or cool from the inside unit. After about 20 seconds, restore power to the outside unit. Go in and turn on the remote and make sure you lower the cool setting more than degrees cooler than the room temp. After 3 minutes the outside unit should turn on. If you get an error code of either 1, 2 or 5 blinks document it for the technician. If you continue to get your 33 and 44, you have a bad control board. If all else fails, press and hold the button located on the lower left side of the art unit and hold for about 5 seconds. If it still no longer works, now you will need the help of someone who knows these units.

Sep 08, 2007 | LG Art Cool LA121CNP wall/window Air...

Not finding what you are looking for?
Mitsubishi Mr. Slim MXZ30TN Air Conditioner Logo

Related Topics:

119 people viewed this question

Ask a Question

Usually answered in minutes!

Top Mitsubishi Heating & Cooling Experts

NOEL
NOEL

Level 3 Expert

8537 Answers

vince

Level 3 Expert

1234 Answers

Stuart Slabber

Level 1 Expert

25 Answers

Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...