York Furnace Draft Inducer Blower Fasco # A224 - Page 3 - Answered Questions & Fixed issues


Check gas pressure, inspect manifold & make sure there is not a blockage.Make sure gas is present and main gas shut off valve to furnace is on also check the knob on the 24 volt gas valve and see if it is in the on position , check the MV terminal on the gas valve to 24 volt common with a volt tester to see if you have 24 volts present, if you do have 24 volts at gas valve, replace valve. if you do not have 24 volts at gas valve check high limit control & roll out limits for a open circuit, Good luck.

York Furnace... | Answered on Mar 04, 2010 | 2,299 views


Check pressure switch for inducer motor. If switch closes, check for crack in ignitor. If gas valve opens and you can hear/smell gas, the ignitor is bad probably. If pressure switch isn't closed you need to check for blocked vent/chimney/heatexchangers.

York Furnace... | Answered on Jan 21, 2010 | 992 views


Flame sensor should be cleaned every 1 to 2 years. The flame sensor is a small silver rod that sits in front of one of the burners. Cleaning it with abrasive cloth will do the trick. Always shut power off first.

York Furnace... | Answered on Jan 21, 2010 | 350 views


Check for a short in the red and white wires.

York Furnace... | Answered on Jan 01, 2010 | 188 views


I had the identical problem with my York. Problem was the burners. The heating element would light the first burner but the flame wouldn't move to the other burners. The flame sensor didn't detect a flame on the last burner so the gas valve would shut off. I removed and cleaned the burners then reversed the first and last.

York Furnace... | Answered on Dec 17, 2009 | 777 views


the motor could be bad or it could be a capacitor that should be mounted on the fan.. check for a rupture on the top where the wires connect or if its round, check to see if it is bulged out. if it were a relay problem, the board should be flashing

York Furnace... | Answered on Dec 16, 2009 | 486 views


Check if they have a "sail switch" that senses combustion air flow before allowing fire. These are a small vane in the combustion air intake that moves a microswitch when air is flowing.

York Furnace... | Answered on Dec 16, 2009 | 306 views


need help with gas furnace put in new presure switch and it worked for a while now i have to blow into it to get it to turn on ignitor .

York Furnace... | Answered on Dec 10, 2009 | 1,003 views


The flame sensor is not sensing the flame. Google "flame sensor"

May be an adjustment or control board problem.

York Furnace... | Answered on Dec 08, 2009 | 335 views


Nordyne Furnace, pilot is lit, thermostat is reset, Heater is on but blowing cold air.

York Furnace... | Answered on Dec 19, 2014 | 1,934 views


Need blower motor for York Diamond 80 Furnace I am in St Louis MO where can i get one

York Furnace... | Answered on Oct 11, 2009 | 1,494 views


you have a bad fan, or something stopping it
your coilsd arfe frosted over becuase they are not getting propper air flow across them

York Furnace... | Answered on Oct 06, 2009 | 219 views


Is it a gas burner? Does it have a pilot light?

I’m happy to help further over the phone at https://www.6ya.com/expert/bob_62dfa2f81bb55288

York Furnace... | Answered on Sep 30, 2013 | 1,297 views


Call that serviceman back!
he did not want to run new wire so; he left you one wire short and, thought you wouldn't notice to fix this yourself i've included the proper thermostat wiring diagram at:
http://www.toad.net/~jsmeenen/wiring.html

York Furnace... | Answered on May 04, 2009 | 568 views


I put a new control board in my York today and it was a different/newer board. I immediately had the 9 code thrown at me for grounding and polarity issue. All I had to do was switch the 2 gray wires on the transformer. The gray wires go the the 12 pin connector. The new board is wired differently.

York Tools &... | Answered on Dec 15, 2015 | 2,304 views


Sounds like a bad thermostat or stuck motor control relay. Turn off the breaker at the unit or in the electrical panel to kill the motor and see if cutting power, if relay is bad, cycles off and stays, but you should leave power off and call for service right away.

York Tools &... | Answered on Jun 18, 2015 | 44 views


Check the relay for that motor. Follow the wires back to locate the relay. If the relay clicks when you advance the thermostat then check the relay contacts with a multimeter. If there is continuity and a low resistance value on the contacts then look at the motor itself. There is a hi limit safety klixon switch that may be holding voltage from reaching the motor too. The wiring diagram should be on or inside an access panel.

York Tools &... | Answered on Dec 31, 2014 | 86 views


Found it on repairclinic website:

Manufacturer Number S1-47320937001

York Tools &... | Answered on Dec 10, 2014 | 61 views


What Light???? More informaton needed.

York Tools &... | Answered on Jul 02, 2014 | 34 views


I would first check the blower to be sure it is ok. If so then the control board would need to be replaced.

York Tools &... | Answered on Jul 02, 2014 | 122 views

Not finding what you are looking for?
York  Furnace Draft Inducer Blower Fasco # A224 Logo

136 questions posted

Ask a Question

Usually answered in minutes!

Top York Tools & Hardware - Others Experts

Brad Brown

Level 3 Expert

18157 Answers

Bob Janelli

Level 1 Expert

26 Answers

djbilo

Level 2 Expert

84 Answers

Are you a York Tool and Hardware - Other Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...