SOURCE: blower fan running constant after new fan and

Here's my best shot.
Check the temperature settings for the fan switch.
The low OFF setting should be about 100 degrees.
The ON setting should be around 150 degrees and this is the setting that "makes" the ON contacts.
The HIGH LIMIT setting should be about 180 degrees.
If these are set, can you use a meter to see if the FAN ON contacts are closed?
Lastly, it appears that one hot line should go to one side of the blower and the other hot line should go to the bottom FAN terminal with the other side of the blower being fed by wiring from the top FAN terminal.
Good Luck. Gary

Posted on Feb 22, 2011

Ad

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Fan will not cut off


Janet, the problem most likely is not in the thermostat. It is probably the fan relay on the circuit board in the furnace. Some furnaces have an individual fan control board, some furnaces have all the controls integrated within one control board. If your furnace is 20 years old or older, it could be the fan/limit control because at that time all furnaces did not come with a control board. If it is much older than 20 years, it is much more likely a stuck fan/limit.

Apr 12, 2015 | Honeywell Programmable Thermostat Heater

1 Answer

Fi have a older furnace that operates like this. main burners will come on then the blower turns on and furnace continues to heat untill it shuts down on the high limit. there is no blockage on the cold...


Maybe there is a blockage in the air conditioning coil above the furnace? This happens when people have pets, or dont use filters. Single phase 120-240 volt motors won't run backwards if you reverse the wiring that's dc or three phase, you have to check the rotation of the wheel, the right rotation is usually marked on the blower case. Some motors will allow you to change the rotation but you have to check the wiring diagram. Also use new capacitors when they go bad the motor can run backward. God luck

Dec 20, 2011 | Honeywell L4064B2236 Fan/Limit Control...

2 Answers

Carrier oil furnace model 58BMA155-20(FORCED HOT AIR)i had changed the blower motor & honeywell st9103a128 fan control board.now the blower motor won't shut off until the breaker is turned off.i...


You need to check the wiring to the limits and safety devices with are in a number of locations, make sure all connections are tight.The most common cause for the blower to run is the high limit device which is the one mounted above the burners on the flat metal panel with two wires.

Nov 03, 2011 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

Blower fan running constant after new fan and limit switch installed.more info.Honeywell-tradeline.L4064B 2210, combination fan and limit control, adjustable fan differential with manual fan switch, flush...


Here's my best shot.
Check the temperature settings for the fan switch.
The low OFF setting should be about 100 degrees.
The ON setting should be around 150 degrees and this is the setting that "makes" the ON contacts.
The HIGH LIMIT setting should be about 180 degrees.
If these are set, can you use a meter to see if the FAN ON contacts are closed?
Lastly, it appears that one hot line should go to one side of the blower and the other hot line should go to the bottom FAN terminal with the other side of the blower being fed by wiring from the top FAN terminal.
Good Luck. Gary

Feb 21, 2011 | Honeywell Heating & Cooling

1 Answer

How does a honeywell L4064b2236 work? It is set up on a Gas hot air furnace with the jumper removed, Three wire connection, black to common white to fan and red to limit. The furnace has a tranformer on...


If the jumper has been removed, then the control is working in the low voltage circuit. Black should be 120v in, White the 120 going out to the fan, and the red or limit wire is (should be) in the low voltage control circuit. Have you looked at the wiring diagram for the F and L Control? If not I will provide a link for you. https://customer.honeywell.com/techlit/pdf/69-0000s/69-0117.pdf

Hope this helps

Nov 16, 2010 | Honeywell L4064B2236 Fan/Limit Control...

1 Answer

Honeywell thermostat TH6110D1021. Blower comes on


Hi, You are right, fan is on a time delay in the heating cycle, and after burners fire that is when this delay comes into play. You have a preset factory temperature that determines the cycle on time for the fan, and the off time after the burners shut down also. This will not be in the thermostat, but in the fan/limit control the is mounted on the face of the furnace, with a probe inserted into the fire box.Depending on how old or new this unit is, will depend on the type control you have.It may be just a high limit switch, or the 1st I mentioned.If so, It rotates in the burner as the temperature rises, to turn the fan on and off.Disconnect power, remove cover, and 2 screws.Slowly remove the control and gently clean the probe. Turn the dial if this one has it and you will be able to hear it click. This click is contacts closing to start fan operation.Reinsert and try again. If problem continues, you will have to replace it.They do tend to stick closed/on, in the heat cycle from time to time and a cleaning sometimes will solve this problem. Not knowing how old this furnace is and type, make it difficult to give you a correct diagnosis, so check this fan control as I have explained, and if your system is of a different type, please let me no so I can correct this problem. Sincerely,
Shastalaker7

Dec 11, 2009 | Honeywell Programmable Thermostat Heater

1 Answer

How to wire it


Hmm this is tricky it depends what kind of furnace you have etc....need more info but basically you supply 120V to the common connection(with the jumper) and from there you would run a wire L1 to the furnace motor from "Load" on the fan side....and the wire L1 from the "Limit" side will power the furnace transformer../..the Limit ios very important and must be wired correctly...I suggest you have an exspert install it
a58a277.jpg
d87ddb6.jpg

Nov 01, 2009 | Honeywell L4064B2236 Fan/Limit Control...

1 Answer

I have an old 1973 Mac 1199 Intertherm propane furnace The burner will come on and it takes a long time for the blower to come on Sometimes the blower wont come on at all and after awile the burner will...


Replace the fan limit switch. It is sometimes mounted in the ductwork and sometimes just below the ductwork in the furnace cabinet. Note where the little arrows are pointing to on the temperature scale so you can set the new control to the same as the old. Usually this control is made by Honeywell and may have three wires going to it.

Oct 20, 2009 | Intertherm Heating & Cooling

1 Answer

Pilot light will not light


Sounds like you may need a new electronic control module. This is a rectangular shaped plastic box that has wires coming out of it. This is what tells the pilot to light on these older furnaces.

Jan 25, 2009 | Honeywell L4064B2236 Fan/Limit Control...

1 Answer

Blower fan runs to long


ther might be dip swiches on the circuit board you might have to change

Dec 17, 2008 | Honeywell Power Humidifier: Furnace...

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

25 people viewed this question

Ask a Question

Usually answered in minutes!

Top Honeywell Heating & Cooling Experts

Bill Long

Level 3 Expert

606 Answers

Paul Carew

Level 3 Expert

3480 Answers

Cindy Wells

Level 3 Expert

6049 Answers

Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...