What are the correct setting on the limit switch for oil furnance? My fan comes on off and back on within 1 minute.

Posted by on

Ad

1 Answer

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Vice President:

    An expert whose answer got voted for 100 times.

  • Expert
  • 279 Answers

The correct setting is whatever setting you want. Set the fan on at some temperature, set the fan off temperature at about 20 degrees below the on setting. If it still runs a short time, either increase the on time or decrease the off time. If the off temperature is comfortable to you then I would suggest increasing the on temp. Do the changes in small steps. Good luck and keep that oil burner tuned...

Posted on Nov 27, 2010

Ad

1 Suggested Answer

6ya6ya

6ya staff

  • 2 Answers

SOURCE:

Hi there,
Save hours of searching online or wasting money on unnecessary repairs by talking to a 6YA Expert who can help you resolve this issue over the phone in a minute or two.

Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.

Here's a link to this great service

Good luck!

Posted on Jan 02, 2017

Ad

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Keeprite furnance showing 7 flashes blower fan on no fire inside furnance


Limit Or Rollout Switch Open--Requires Manual Reset.
Read Sticker On Unit--Codes Are There.

Mar 07, 2015 | Heating & Cooling

1 Answer

My furnance keeps turning off and I could go to furnance flip switch on and it only last 5 minutes then shuts off again


You may want to check the limit switch or you could have a issue with the gas valve or transformer. I would check the low voltage transformer first, Sometimes I have found that under load the transformer will open ( quit working) and will close after power is removed and it cools down, It indicates a bad internal connection.

Jan 26, 2013 | American Standard Trane Ge Gas Furnace...

1 Answer

My Ruud furnace used to regulate 1 deg +\- the set temp. Now it regulates right at the set temp and the fan cuts off while the burner continues to fire for a minute or so then the fan kicks back on for...


Hi,
It appears to be the fan limiter switch. It comes on at a certain temp when heating up and shuts off on the high end of its setting. Once the burners are shut down, the fan continues for a few minutes to cool down the burners. The limiter switch is adjustable but it sounds to me to be defective and should be replaced. Good luck and stay warm, :-)

Mar 15, 2011 | Ruud Heating & Cooling

1 Answer

Hi,my name is julio i have a problem with my goodman furnance,the furnance run for 10 or 15 minutes and then shut off and come back again for 5 minutes keep do in on and off on and off and then shu off...


it is probably hitting the high limit switch possibly.
Is your filter clean?
Are all the vents in the house full open?
Is your furnace vent (flue Pipes) clean and unobstructed?

Jan 07, 2011 | Goodman GMS90703BXA Heater

1 Answer

Weathermaker 8000 furnance flashing code 31 blower comes on for 90 sec .. then shuts off .. then other fan goes on.. don't see any flames or lighting goin on can you help?


31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than five minutes,
inducer shuts off for 15 minutes before retry. Check for: - Excessive wind
- Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used) - Restricted vent
If it opens during blower on-delay period, blower will come on for the selected blower
off-delay.
33 LIMIT CIRCUIT FAULT - Indicates

Nov 04, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

Coleman furnace and the fan takes awhile to come on then runs for about a minute then shuts down. im thinking the fan cycling switch was moved and now takes longer to reach temp


If it operates on a fan/limit switch it is possible the settings are wrong. Typical settings are: Fan Off-110F Fan On-140F High Limit-170F. If these are correct, you probably have a bad f/l switch. The bi-metal spring in these switches fatigue and will not rotate the switch smoothly.

Oct 03, 2009 | Heating & Cooling

1 Answer

Limit Switch


It is rare that a limit switch goes bad. It is a safety control. If it is shutting off your furnace there is a problem that it is protecting you from.
If the limit switch is shutting the unit down your furnace is overheating. Check the filters. Check for any obstruction in the blower assembly. Check to see if you can raise the blower speed. Make sure all registers are open in the house. Your evaporator coil could be obstructed if you do not take good care of your filters.

Feb 28, 2009 | Goodman GMS90703BXA Heater

1 Answer

Progrmmable Thermostate


Check to make sure you have pm or am set correctly. Or reset everything. ??? ;)

Dec 13, 2008 | Hunter Fan Company 5/1/1 Programmable...

1 Answer

Hello my name is veronacarrier 8000 weathermaker will not ignite


call the furnace repairman. you have a fairly easy repair but the parts are expensive

Dec 13, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...

1 Answer

Furnace come on then fan stops while burner still is on, then fan comes on for 1 min. and goes off over and over


This could be a couple of things, first is the fan limit switch. Make sure your fan limit is set at the correct settings, there is a fan on setting and a flame shut off setting located on the front of air handler inside the front cover. Usaully set at 140 fan on 200 gas shut off. You do not say what unit you have so this could be a pc board or module. Second this could be the blower it's self over heating and shutting down, feel if motor is gettig hot. This could be a run cap. or motor it's self. But it is more than likely the limit switch.

Sep 29, 2008 | Coleman Heating & Cooling

Not finding what you are looking for?
Honeywell L4064B2236 Fan/Limit Control Heater Logo

Related Topics:

167 people viewed this question

Ask a Question

Usually answered in minutes!

Top Honeywell Heating & Cooling Experts

Bill Long

Level 3 Expert

606 Answers

Paul Carew

Level 3 Expert

3484 Answers

Cindy Wells

Level 3 Expert

6065 Answers

Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...