Protection against AC overcurrent E5

"Switch the appliance off and on again. If this does not resolve the issue, contact an Authorised Service Centre."

Free service manual for an Electrolux appliance.

https://www.manualslib.com/manual/824502/Electrolux-Exh09hl1w.html?page=31


Electrolux EXH09HL1W Service Manual Error Codes



Quoting from a service manual:

https://www.manualslib.com/manual/824502/Electrolux-Exh09hl1w.html?page=46#manual


"(6) Over current protection
E5 is displayed on indoor unit
Yellow LED lamp of outdoor unit blinks for 5 times
#It indicates that the current of the complete unit is too large. Check if voltage of power supply is normal."




Electrolux EXH09HL1W Service Manual Page 46

Electrolux... | Answered on Aug 21, 2018


good day I have a problem with my aircon its ECOAIRE aircondition with error F6

Electrolux... | Answered on Jun 11, 2018


Anti high temperature protection.
Check the outdoor coil for airflow obstructions.
Check the outdoor fan motor for correct operation.

Electrolux... | Answered on Apr 14, 2018


it can damage the motor solenoid. looks similar to these
motorwiring-cjpkdpr3r0ttdxwtzkam4apy-1-0.jpgpower goes into the capacitor and turns the motor on at a steady speed and builds up power, if it overloads that can happen it will either send full voltage that the motor cannot build up on or no voltage

Electrolux... | Answered on Feb 22, 2018


Indoor pipe sensor (thermistor) fault. These are cheap and easy to replace.

Electrolux... | Answered on Oct 02, 2017


H6 indoor unit fan stall.
Most likely a faulty fan motor but could be a faulty controller board. My money is on the fan motor which is a DC motor.

Electrolux... | Answered on Oct 02, 2017


Remote screws holding front panel on the head unit. There are usually 2 - 4 at the bottom of the louvers (for a split system) and possibly a couple under the panel that hides the filters. The whole front panels should then be able to easily lift up from the bottom and un-clip from the top.
DO NOT FORCE it if it doesn't come off fairly easily, as the plastic will break. Check that you haven't missed any screws.
Once the panel is off (make sure power is off to the whole unit) just un-clip the Rx board from the controller and plug in the new one. The Rx board may also be held by screws or just plastic clips.

Electrolux... | Answered on Oct 02, 2017


I'm not sure if all electrolux share the same error code table but most manufacturers have a common error report table for all of their own models. If that is the case, F2 is a indoor pipe sensor thermistor short/open fault. These are cheap and easily replaced.
If you have a multimeter, you can test the resistance of the pipe thermistor by disconnecting from the controller board and testing across the connector terminals of the thermistor wires. Resistance values are in the table attached.
You may have to get the service manual to be certain.


thermistor values-tuffkldngvhkjdjea0eugjkm-4-0.png

Electrolux... | Answered on Oct 02, 2017


Press the temperature (increase & decrease) buttons simultaneously for 3-4 seconds.

Electrolux... | Answered on Jun 23, 2017


Compressor high temperature cut out. Possibly the heat exchanger on outdoor unit is clogged with dirt which you can clean with a gentle spray from a hose. Other possibilities: - electronic expansion valve is faulty (if fitted); or refrigerant is low which means you have a leak.

Electrolux... | Answered on May 03, 2017

Not finding what you are looking for?
Electrolux Logo

169 questions posted

Ask a Question

Usually answered in minutes!

Top Electrolux Heating & Cooling Experts

Brad Brown

Level 3 Expert

18121 Answers

Superior Maintenance

Level 2 Expert

67 Answers

Steve F

Level 3 Expert

1360 Answers

Are you an Electrolux Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...